I tried a little experiment with two Nions, both running 1.6.5 firmware and both running no roles.
I put both in Normal time sync mode and then changed the time to be very different on one NION and saw the other track the new ime instantly. I tried this with both units and the time always updated properly.
I then set one unit to be master and changed its time and the other Normal mode device tracked instantly.
Then I changed the Master to NTP mode and specified an NTP server. The NTP device time then updated to the correct time right away and the Normal device also tracked that update instantly.
In short, I found no problems at all.
Can anyone having this problem provide more data?
There is obviuosly something different between my test setup and those seeing the reported problem
How many devices are in the net? What kind of projects are running?
Any non-standard settings of any sort?
There is obviously a difference in test setups that we must identify in ordere to reproduce and anlyze the problem.
Can anyone attach a project file under which this problem is seen?
Or send it to me.. sgray@peavey-eu.com
Also, can anyone who has the problem try reproducing my scenario? (2 NIONS, 1.6.5, no roles)
Nihilism is best done by professionals